It is about the electrical system in the US not being able to supply water heaters in dishwashers and washing machines.

That is a myth arising from US typical residential circuit standard being 20A @ 120V, or 2400W.

Major appliances are not limited to this typical standard. US/Canada have code for and commonly install dedicated 30A@120V, (commonly used for large through-window air conditioners) as well as 240V circuits rated from 20A to 80A. The North American electrical system typically provides 200A @ 240V to the residence. That’s sufficient for heating hot tubs and in-ground pools.

No, the decision to use hot water instead of cold water arises primarily from plumbing factors, not electrical.